Reply To: System Startup Problem 3 PID loops

#3719
WhiskyjimJim Manley
Moderator
  • Topics: 19
  • Replies: 47
  • Total Posts: 66
Karma: 241
Rank: Jedi

Would it not be possible to run the PID that controls the feed temperature valve in Override or Hand mode with a set CV, while monitoring the water temperature then switch back to Auto mode once you’ve achieved the water temperature you need for successful start up?