- February 7, 2019 at 12:19 pm #3714
whiskyjim
ModeratorKarma: 262Rank: JediDoes anyone know where I can find a list of what the AB PIDE status words mean? I’m working on a model and the PIDE is locked into Manual mode and displaying a value of 16#0000_0061 in the Status 1 parameter.
I’ve searched around the internet and Rockwell’s tech support site but am drawing a blank.
Thanks,
Jim
February 8, 2019 at 1:19 pm #3715mrincredible
ParticipantKarma: 53Rank: PadawanHi Jim.
The bit mappings for this “Status1” word can be found in the builtin Studio 5000 help file. I’ve created a little PDF for your convenience attached here. A value of 61 Hex is equal to the following binary 0110 0001. So you have three flags set in this status word: bit 0, bit 5 and bit 6. Looks like its a configuration problem with your Setpoint Limits. The information for the Status1 word information starts on Page 7.
Hope that helps!
Attachments:
You must be logged in to view attached files.February 11, 2019 at 4:30 pm #3718whiskyjim
ModeratorKarma: 262Rank: JediThanks for the response. I actually stumbled across the help file about 10 minutes after I submitted my original post. Funny how it works that way.
Jim