Burkert 8792 valve feedback

https://www.linkev.com/?a_fid=ics-eng

This topic contains 1 reply, has 2 voices, and was last updated by Nikhil Mahesh Nikhil Mahesh 1 week, 3 days ago.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #7709
    Arjun Kr
    Arjun kr
    Participant
    • Topics: 2
    • Replies: 2
    • Total Posts: 4
    Karma: 24
    Rank: Padawan

    Hi,

    I have an Burkert control valve( type 8792) , a devicenet device and I’m trying to read whether the device is in automatic or in manual mode( essentially the operating mode) as this isn’t in the default set of inputs that you obtain from the control valve.

     

    Thanks,

    Arjun

    #10854
    Nikhil Mahesh
    Nikhil Mahesh
    Participant
    • Topics: 1
    • Replies: 3
    • Total Posts: 4
    Karma: 16
    Rank: Padawan

    Refer to https://www.burkert.com/en/Media/plm/MAN/MA/MA8792-Standard-EU-EN.pdf?id=MAN0000000000000001000118577ENI

    This is manual for the control valve. See page 220 about online parameterization. Infact if you look at the screenshot you should be able to spot Operating Mode. After completing the configuration you should be able to access it with the device net data set of the device.