- January 19, 2018 at 8:23 am #1132
WaseemParticipantKarma: 11Rank: PadawanI have a problem with importing tags of data log models i get a comma at end of each tag name. Had anyone face this problem and kindly tell me solution will be very thankful.
January 19, 2018 at 8:57 am #1133
tfgmedia_adminKeymasterNew Topic Thread started for you.
January 19, 2018 at 11:24 am #1140
tfgmedia_adminKeymasterHi Wasseem,
There is technote on the issue you are facing here if you have a techconnect contract you can view it otherwise see below.
Cause
The Regional and Language settings was configured for a country that does NOT use the comma
,as a List Separator. When a Data Log Configuration CSV file is imported, this appends the,on each of the tag.Solution
- Change the Regional and Language Settings to English – United States
- Reboot computer
- Import the CSV file again to the Data Log using Import Tag List Overwrite
January 20, 2018 at 12:27 am #1173
WaseemParticipantKarma: 11Rank: PadawanThanks guru i will give it a try on monday and will tell you.
January 28, 2018 at 1:44 am #1264
WaseemParticipantKarma: 11Rank: PadawanThank you sir I have tried your solution but it did not work for me. But I used a little trick that worked for me.The trick was that if you import datalog model tags and you see a comma after each tag then you have to click option remove all and then click add all in datalog model popup. You will get all tags without comma.
January 28, 2018 at 10:16 pm #1266
tfgmedia_adminKeymasterHi Waseem,
Glad you got it sorted. And thanks for sharing the tip!
Cheers!