› PLCGurus.NET Live & Interactive Forum › PLC Questions and Answers › Rockwell, Allen-Bradley, Stratix › Factory Talk View Studio: Problem Importing Datalog Model Tags
Tagged: Factory Talk View Studio
- This topic has 5 replies, 2 voices, and was last updated 5 years, 8 months ago by
tfgmedia_admin.
- AuthorPosts
- January 19, 2018 at 8:23 am #1132
Waseem
ParticipantKarma: 11Rank: PadawanI have a problem with importing tags of data log models i get a comma at end of each tag name. Had anyone face this problem and kindly tell me solution will be very thankful.
January 19, 2018 at 8:57 am #1133tfgmedia_admin
KeymasterNew Topic Thread started for you.
January 19, 2018 at 11:24 am #1140tfgmedia_admin
KeymasterHi Wasseem,
There is technote on the issue you are facing here if you have a techconnect contract you can view it otherwise see below.
Cause
The Regional and Language settings was configured for a country that does NOT use the comma
,
as a List Separator. When a Data Log Configuration CSV file is imported, this appends the,
on each of the tag.Solution
- Change the Regional and Language Settings to English – United States
- Reboot computer
- Import the CSV file again to the Data Log using Import Tag List Overwrite
January 20, 2018 at 12:27 am #1173Waseem
ParticipantKarma: 11Rank: PadawanThanks guru i will give it a try on monday and will tell you.
January 28, 2018 at 1:44 am #1264Waseem
ParticipantKarma: 11Rank: PadawanThank you sir I have tried your solution but it did not work for me. But I used a little trick that worked for me.The trick was that if you import datalog model tags and you see a comma after each tag then you have to click option remove all and then click add all in datalog model popup. You will get all tags without comma.
January 28, 2018 at 10:16 pm #1266tfgmedia_admin
KeymasterHi Waseem,
Glad you got it sorted. And thanks for sharing the tip!
Cheers!
- AuthorPosts
- You must be logged in to reply to this topic.