      Need help. How to wire Fault Relay contact ?

      See attached screenshot. R2C is common & R2A is normally open contact.

      When VFD drive gets faulted or not running, I would like to get input to Micrologix PLC.

      Do I need to provide +24Vdc to R2C ? Let me know

       

      Thanks !

      Attachments:
      You must be logged in to view attached files.
      #2639
      jones124000jones124000
      Participant
        Karma: 171
        Rank: Jedi

        Hello RAJ,

        If your 24VDC input card has a common of 0vdc or neg(-) of the power supply you are using then you need 24VDC+ on either contact. The other contact wire should go back to the input terminal you want to use.

        Hope the pic came out OK. See Attachment

         

        Attachments:
        You must be logged in to view attached files.
        #2653
        XavierXavier
        Participant
          Karma: 11
          Rank: Padawan

          Thanks a lot