- February 15, 2021 at 7:57 am #20103
Rowdy
ParticipantKarma: 31Rank: PadawanIs it normal to get the fault ‘External Fault – Ethernet link disconnected’ when there is no Ethernet plugged into the network card? It goes away when we plug any device into it but i could not find any info on this from Schneider documentation.
February 18, 2021 at 10:37 am #20105tfgmedia_admin
KeymasterHi Rowdy and welcome to the forums.
To me, this doesn’t seem like an inaccurate fault since as you say the Ethernet cable is unplugged. The controller is probably doing a “heart-beat” type check (or more likely sending an ARP packet out periodically) to see whether its network connection is active or not.
Then as you say, the fault goes away when it detects that it’s connected to a network. It doesn’t seem to me that this is something you should be concerned about, in fact, you may want to consider monitoring this fault in your logic to annunciate it in the event it does occur when you least expect it!
Cheers
Fred
February 18, 2021 at 1:21 pm #20106Rowdy
ParticipantKarma: 31Rank: PadawanThanks, it seemed normally from me but I could not find anything about it in Schneider’s documentation referring to it. It was scaring the operators so I already went ahead plugged an unnecessary cable into it to make the red lights go away.