- September 7, 2018 at 3:28 pm #3257
Alex
ParticipantKarma: 14Rank: PadawanI am attempting a simple NAT with two ControlLogix PLCs; both L73S, with the Stratix 5700 8 port 10CGN
PLC1 ip address is 10.0.103.4 gateway 10.0.103.1, this controller has exclusive connections to devices
PLC2 ip address is 192.168.1.4; gateway 192.168.1.1, this controller has a connection to 5700. devices are inhibited.
Devices to translate:
1723ES ArmorBlock safety IO 192.168.105; NAT 10.0.103.5
284ES ArmorStart motor starter 192.168.1.22; NAT 10.0.103.9
1732E-8CFGM8R ; 192.168.1.79; NAT 10.0.103.7
1732E-8IOLM12R ; 192.168.1.125; NAT 10.0.103.8
I setup smart ports, enabled layer 3 routing per your videos, setup port configuration, VLan mgmt. etc. RSLinx is unable to discover any of the NAT addresses. All of the devices are on Eth1-IP and Eth-1. which is the 192.168.1 network. RSLinx can communicate with all.
Eth2-IP is the 10.0.103 network and only 10.0.103.4 the EN2TR is visible. No NAT devices on Eth-2 are visible.
There is NAT taking place because I have a connection to the ArmorBlock at .105 and the ArmorStart at .22. The motor is spinning. I am unable to connect to the IOlink at .125 or the 8CFG at .79. Connection timeout errors in the AOP
NAT only works if I setup the Public to Private configuration, see file nat config2 From the EN2TR at 10.0.103.4 to the 5700 at 192.168.1.2 The gateway NAT does not have any affect. I can delete it and the connection remains to the ArmorStart. If I delete the Public to Private NAT, the connection breaks.
What should I try next?
Attachments:
You must be logged in to view attached files.September 10, 2018 at 9:35 pm #3291tfgmedia_admin
KeymasterHi Alex,
Welcome to the forums! You had this posted in the “Practice Posting” forum which is why I wasn’t notified. Do you have any error on your switch in the bottom status bar i.e., uplink port is blocked or something along those lines? A drawing of your layout would be helpful to visualize too, even if it’s a sketch or something.
Fred